Why we should change our building air tightness metrics
The discussion about building air tightness often becomes abstract, but it is crucial for building standards, ranging from best practices like Passive House to minimum requirements set by the National Construction Code. For decades, Passive House has used air changes per hour at 50 Pascals (ACH50) as its standard. However, there is a compelling argument that this metric might be inappropriate for various building types.
The AIRAH Special Technical Group in Building Physics suggests that air tightness results should be expressed in terms of air permeability of a building envelope. This metric measures the amount of air leaking through every square metre of the building's surface area (walls, floor, and ceiling), typically expressed as qE50 or m3/hr·m2. A potential target for the National Construction Code is 10 m3/hr·m2 @50Pa. While ACH50, which divides air leakage by building volume, may seem similar, the author illustrates that for typical houses, the surface area and volume metrics coincidentally yield similar results. For instance, an average of 13.7 ACH50 in 130 Australian homes nearly equated to 13.8 m3/hr·m2 permeability.
The discrepancy becomes significant when considering commercial buildings. The author explains that surface area scales with the square of a building's dimension, while volume scales with the cube. This means that as buildings get larger, their volume increases much faster than their surface area. A commercial building might have six times more volume than surface area. Consequently, a larger building would more easily meet an air tightness standard based on volume (ACH50), even if its construction quality is not superior. This highlights a flaw in using a volume-based metric for diverse building sizes.
From a building science perspective, the argument for a volume-based metric, such as heating the building's air volume, is technically incorrect. Heating energy is primarily expended on replacing leaked air, not the entire static volume. A thought experiment involving a blower door test with a large balloon inside a house demonstrates that leakage rate is related to the surface area, not the internal volume. The leakage rate remains constant regardless of the volume occupied by internal objects, much like the flow rate from a container with a hole depends on the water height (pressure) and hole size, not the container's overall volume. While a smaller volume container might lose water faster, the energy required to heat the water to a constant temperature depends on the flow rate, not the static volume.
The author acknowledges that minimizing surface area per unit of living space is an effective energy conservation strategy, as more surface area leads to greater heat loss. However, when assessing the quality of construction, the focus should be on the workmanship of the envelope itself, rather than the architectural design choices that dictate surface area. A surface permeability standard aligns with this principle, similar to how insulation standards specify a minimum thickness per square metre of surface area.
Regarding the simplicity of calculation, some argue that a volume-based metric is easier to compute. While this might hold true for simple, flat-ceilinged houses, it becomes complex for buildings with intricate rooflines or multiple stories. Modern software tools like Google SketchUp can easily calculate both surface area and volume, negating the argument of computational difficulty. Furthermore, professionals like NatHERS assessors already calculate surface areas for energy models, suggesting that integrating surface permeability into air tightness assessments would not necessarily add extra work.
In conclusion, the article advocates for a shift from volume-based (ACH50) to surface-based (permeability) metrics for assessing building air tightness. While both metrics may be similar for houses, permeability is more scientifically sound and universally applicable across different building scales. It more accurately reflects the quality of the building envelope's construction and aligns better with existing energy efficiency assessment practices.
#BuildingAirTightness #ConstructionStandards #PassiveHouse #AirPermeability #EnergyEfficiency #BuildingPhysics #NationalConstructionCode #BuildingEnvelope #BlowerDoorTest #BuildingAirTightness #ConstructionStandards #PassiveHouse #AirPermeability #EnergyEfficiency #BuildingPhysics #NationalConstructionCode #BuildingEnvelope #BlowerDoorTest